Replies: 2 comments 1 reply
-
Probably you enabled DEBUG in the config file. |
Beta Was this translation helpful? Give feedback.
-
Thank you very much for the solution. Yes I did. I have made an update and after I did that, the second BMS dosen't work. Then I enabled Debug. In the log-file, I found a line: instance or Id of the BMS was found twice. Then I changed the capacity in the config of the BMS from 2800000 to 281000 and everything was fine. But my real problem is that the current limitation doesn't work. That's why I uninstalled the battery aggregator, then disconnected the second BMS. Enter the serial battery in DVCS and system setup. In the config MAX_BATTERY_CHARGE_CURRENT = 2.0 set to 2 A. My expectation is that it will then only charge with 2 A. But it loads what the panels have to offer. Am I wrong or have I overlooked a setting? Fred |
Beta Was this translation helpful? Give feedback.
-
I just updated serial battery, last version. Setup no. 1.
Now the screen under parameter is confusing. Before I had one line after the other.
Then I updated it again to the beta version 1.2.20240227beta. Same screen.
I thing I can not make anything wrong.
JBD BMS 16S
Any idea, was is going on?
Fred
Beta Was this translation helpful? Give feedback.
All reactions