Use the template below if you have an issue or want to report a bug. If you have a question or a feature request you can ignore the questions below. This is a template so feel free to remove any of this text. Try to include the info below when applicable. NOTE: If you are having issues with your serial connection, please read this page before posting: https://github.com/jgyates/genmon/wiki/3.6---Serial-Troubleshooting If you are having other issues, please see the following page: https://github.com/jgyates/genmon/wiki/3.5---General-Troubleshooting You can search past issues by removing the "is:open" keywords from the search window and adding any keywords that are relevant to your issue. If you need to send you logs and registers to the developer, if your email is setup and working properly you can click send your logs on the About page in the web interface. Expected BehaviorIt is expected for the generator to run normally at the correct RPM and frequency during the Daily Enhanced Exercise, similar to its performance when turned on via the controller Manual exercise via the maintenance page in the portal. Actual BehaviorDuring the Daily Enhanced Exercise scheduled at 10:30 AM daily, the generator's RPM is lower than expected, running at less than 2500 RPMs, whereas it should be around 3600 RPMs to match the normal operational standards. There are no error codes displayed when this issue occurs. Steps to Reproduce (including precondition)
Screenshot or Pictures relating to the problem (if possible)N/A Your EnvironmentGenerator Model: Generac 8KW/410 GUARD+10C T/SW - Model: 0058701 |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 3 replies
-
What you are describing is normal, assuming you have the Quite Mode exercise cycle selected. There are three modes for the Enhanced Exercise Add on: Quite Mode, Normal and Transfer. Quite Mode will run at a reduced RPM and output voltage. This is a feature of the controller. The built in exercie cycle has the option of doing this as well. Let me know if you have any questions. |
Beta Was this translation helpful? Give feedback.
What you are describing is normal, assuming you have the Quite Mode exercise cycle selected.
There are three modes for the Enhanced Exercise Add on: Quite Mode, Normal and Transfer.
Quite Mode will run at a reduced RPM and output voltage. This is a feature of the controller. The built in exercie cycle has the option of doing this as well.
Normal will run at full speed (3600 RPM for Air cooled models)
Transfer will run at full speed but also engage the transfer switch.
Let me know if you have any questions.