My generator had an under voltage error and was only outputting 75V. The repair required replacement of the control board. It's a 22kw Generac with Evolution 1 controller. It was replaced with same controller. After this new controller, GenMon is repeatedly cycling through alerts "Not receiving data" and then "Health OK" (via Slack integration). Looking at monitor data, it shows 17-20% timeout errors under Communication Stats. Any advice for troubleshooting? |
Beta Was this translation helpful? Give feedback.
Replies: 3 comments 6 replies
-
are you using serial or serial over TCP? If serial over TCP are you using WiFi? |
Beta Was this translation helpful? Give feedback.
-
Thanks, this status update helps others who may have the same type of issues. Let us know how it goes. |
Beta Was this translation helpful? Give feedback.
-
I am glad it is working for you. Thanks for the update. |
Beta Was this translation helpful? Give feedback.
Definitely an issue with serial comms after running the serial tests. Looks like my cable is a combination of a DB9 connector plus 2 of these connected together. The DB9 and RS232 serial connection to the Pi looks good. I may just replace those 2 molex cables and see if that resolves the issue.