Generac 24kw
#1131
-
Checklist
VersionLatest Have you submitted your log files from the About page? Note that outbound email must be working for logs to be submitted.I have not submitted logs What is/are your question(s)?Why does the amp meter redline at 50 amps when the generac 24kw is good for 100 amps? Additional informationNo response |
Beta Was this translation helpful? Give feedback.
Answered by
jgyates
Jun 2, 2024
Replies: 1 comment 5 replies
-
I may be able to answer this, I might need more info to answer your questions.
The reason the max current is divided between 2 legs is due to the design of the generator. Each leg has an unbalanced capacity of 50% of the total capacity. |
Beta Was this translation helpful? Give feedback.
5 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
@rwskinner
They way it is displaying is correct for your generator. The addition of L1 and L2 gauges and the load imbalance detection were added at different days so I it is possible that the version you had previously was displaying incorrectly. I recall making a change that corrected the L1, L2 max current between 1.19.2 and 1.19.3.