Hello @indiatce :D and welcome! So, to do what you desire to do, I'd recommend you to add a constrain with extra_functionalities to make sure that the charging power of your converter (be it the storage_unit or the charging link) is lower than the available production by the carrier of interest in every time step. To create unidirectional links, you need to specify p_max/min_pu accordingly: one being 0 and the other one +1 or -1, depending on what bus0 and 1 you specified. |
Beta Was this translation helpful? Give feedback.
-
I want to charge my storage unit by a particular carrier, which can be either grid or solar or wind. How to apply constraints in the CSV files for the storage units such as 'storage_units', 'storage_units-inflow' and 'storage_units-state_of_charge_set', or in the code. I tried to connect the storage unit with uni-directional link, but the links are not working in unidirectional mode. Can you please suggest me, how and where can I implement such constraints so that my storage unit gets charged by a particular carrier, even if it is interconnected with the other buses (both generator and load).
Beta Was this translation helpful? Give feedback.